Siemens IB to QB transfers
bdb1324
Jul 2019
b
16
In Siemens s7-300 are IB and QB calls internal bytes or would QB17 overwrite Q17.0 through Q17.7 ect?
QB17 would overwrite Q17.0 through Q17.7.
Similarly, QD16 would overwrite QB16-QB19 (which would be Q16.0-Q19.7 or QW16-QW18).
Thank you that clears up a lot for me. So another example B#16#3F is in hex when it gets transferred to QB17 will it be in binary form or decimal or hex?
Bin vs Hex vs Dec is just how you view the number. It's all the same to the PLC. You pick how you view it, just like you can in the windows calculator.
I guess what I meant was will it store it as
qb17 0 0 0 0 0 0 0 3F
qb17 0 0 0 0 0 0 0 63
qb17 0 0 1 1 1 1 1 1
I am perplexed by this QB is the same. i.e. Bit Q 0.0 is the first bit of QB0 so why would you transfer it, on the other hand transferring a IB to QB will overwrite the QB with the exact data in IB. If you are talking about I/O refresh then PIB (the actual real Input Image) transferred to IB will update the internal image at that period in time, The real input image is transferred to the internal image outside the normal scan of the code (Dependant on type of PLC) i.e. Before or after code scan the input/output image is updated. If the program scan is 100ms then the Images will be updated every 100ms, however calling a block that updates the I/O image (L PIB 10 T IB 10) will update it immediately, There can be various ways to update, Calling the update function in an interrupt or by calling the FB many times in OB1 between calls to other blocks. Calling it in interrupt will update either in I/O interrupt (update when real inputs change) or if say scan of PLC is 100ms calling the block many times in OB1 will update in the following manner
OB1 total scan of PLC 100ms
JU PB X (5ms)
JU FB Update
JU PB y (10ms)
JU FB Update
JU PB Z (15ms)
JU FB Update
Would update the image after 5ms, 10ms & 15ms etc.
IB and QB are not internal bytes - MB are internal bytes. QB 17 consists of Q17.7 to Q17.0 (most significant bit to least significant bit). 8 bits = 1 byte
IB is Process Image Input Byte
QB is Process Image Output Byte
PIB is Peripheral Input Byte
PQB is Peripheral Output Byte
The scan sequence for the S7-300 (with MMCs) is as follows (simplified for this thread):
Write to Process Image Outputs
Read from Process Image Inputs
Execute Code (OB1 & any other OBs for interrupts, timed interrupts, etc.)
Repeat
Peripheral Inputs and Peripheral Outputs are immediately read from and written to the physical I/O at the very spot in the program where they are encountered.
Process Image Inputs and Process Image Outputs are read from and written to the physical I/O at the beginning of the scan.
There isn't really anything more to it than that... other than you can have multiple Process Images in some CPUs, but that's a bit more advanced than the question of this thread.
Thanks everyone for the comments that was a huge help. The program calls FC41 to measure the width of a plate for blasting and painting. Once that is done the program uses a transfer from IB9 to QB17 if the plate is between a certain width if not the program transfers B#16#3F to QB17. Reason for the questions.
FC41 only gets called when the plate is at a certain position on the conveyor.
Thanks for all the information. They are transferring it to an Allen Bradley PLC and I am trying to understand what the Siemens PLC was doing. So very much appreciated.
According to Siemens FC41 is a communication block (FTP) as standard, however it can be changed to another FC number, If it is the original then there must be some communications going on. FC 41 is also reported to be a PID (which if I remember correctly I have used). If you can open it, it may be that it is one created by the programmer. It seems a bit confusing to me. It sounds like they are not using interrupts for counting purposes (unless it is done elsewhere) but are transferring the data to outputs like some parallel interface i.e. a value that represents the size.
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
124
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
81
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
171
192
Hi all! Please inform me if i can make programing of the HMI SIEMENS IPC477D from TIA Portal software or not? I do not have WINCC software but...
112
