Siemens Oold LOGO24 Backup help

usedplcs

Member
Join Date
Nov 2010
Location
Kent, England
Posts
36
HI,

We have an old Logo24 6ED1 052-1CC00-0BA5 which has a memory module in it and I have been asked to back this up.

If I copy the program from Module to logo when ever I remove the module it says no program.
How do I get a backup on PC "Logo!Soft Comfort V6.1.16)

Many Thanks
 
Hi,

As soon as I take the memory module out to connect the Logo cable I get the message no program. This happens even if I transfer from module to Logo?
 
I'm sure this mode for the memory module was selected in your case:

Protected program module (card)
A circuit program is protected when it is transferred from a
protected program module (card) to the LOGO!.
To execute this circuit program in LOGO!, the protected
program module (card) must remain inserted during RUN,
i.e. the circuit program stored on the program module
(card) can not be copied to other LOGO! devices.
Over and above that, a protected circuit program is write–
protected.
 
Many thanks for your time on this issue.

Well, if we can't back the module up then I will need to start from scratch as we can't afford not to have a backup. Will look into this when back in the office Monday.

Thank you again,
 

Similar Topics

Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
94
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
323
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
168
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
321
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
132
Back
Top Bottom