Siemens S210 download parameters From tia Portal program

stu

Member
Join Date
Aug 2005
Location
England
Posts
786
Hi guys
I have a machine with several s210 converters which has the parameters stored on the plc Tia program
Has anyone got a step by step instructions on how to download the parameters to a new drive? Via tia Portal program
The drive Automatically finds its ip addresses?
Any ideas thanks
 
Stu
To download to a new S210 the new S210 has to have firmware 5.2
Then using Startdrive, connect and assign the IP. (I do the pn name too)
Use the PN ports at the bottom. Not the one at the very top
That’s about the gist of it.
Try that and let us know
 
Hi in the existing program the drives are in the tree
And you can go online diagnostics, parameters ect I’ve been told that the parameters can be downloaded from the program and the IP address is assigned via topology?

Just a though if I highlighted the converter and go online with the go online tab in the tool bar at the top of the screen - will it prompted me to load settings and download??

Thanks stu
 
Just a though if I highlighted the converter and go online with the go online tab in the tool bar at the top of the screen - will it prompted me to load settings and download??

I've never seen that... typically, you have to intentionally download by highlighting the top level of the S210 drive in the project tree, and click the download icon. This will download everything from your project to the drive.

Try doing a screenshot with the Snipping Tool program by clicking "New" and drawing a rectangle around what you want to show, then save the file as a png or jpg, then upload it.

How to use the Snipping Tool
 
Last edited:

Similar Topics

Good day Wanting to learn about servos, I bought from Ebay, a USED Siemens Sinamics S210 servo drive with the 1FK2130-2AG00-2SA0 motor. The unit...
Replies
2
Views
1,532
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
Replies
10
Views
105
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
81
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
Replies
9
Views
169
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
5
Views
192
Back
Top Bottom