I have been given the task of monitoring an old Siemens S5-100U that is operating a critical peice of equipment. We are in the process of upgrading this equipment, but until that occurs I need to attempt pulling live data off of the PLC for data logging. I have been able to communicate with the PLC and pull off the existing program. I can see which data bits I would like monitor on the code. Does anyone know if you can, or how to monitor or collect data live?
Thanks in advance.
Thanks in advance.
That means that you've already got a working cable.
Google for OPC + AS511.
Kalle
Yes I do have the "fancy" Siemens cable and DOS based software. (I got them off of EBAY for about $60 total) They seem to work good so far. I am currently using Red Lion G3's for interfacing, but I am not impressed with the data acquisition capabilities. I am probably going to look into National Instruments for faster data logging, etc. However, if I can use the Red Lion to talk to the S5 then I will leave it in place.
Hi!
The programming interface and the AS511 protocol has very limited capabilities. The speed is max 9600 b/s, and 3-5 packets / sec. You can only access one data area per telegram, so it is wise to pack the com-data in one or few DBs. Can't help you with RedLion - unknown for me.
Kalle
Hi!
Kalle
Thanks for the info. I am curious though, what have you used to communicate live with the S5? I have a spare S5 I would really like to set up a test with to see if it is even worth while implementing on the factory floor. I guess I could use Hyperterminal/Telnet on my PC...that might be overly complicated...
This is old gear, so I wouldn't spend much time on it just for fun. I've hardly ever used 100U with communications, except maybe the OP396. And as far as I can recall, it was possible to connect the Sinec L1 (the grandmother of Profibus) to it. The 95U had the same IO-system, had much more power, RS232 comm. possibilities and was far more popular. I myself have mostly used the bigger 115/135 and 155U with serial, Profibus FDL or Ethernet comms.
The hyperterminal will not bring you any data via the unbelievably nasty 511-protocol. It has sw-handshakes and narrow timing parameters and is secret to Siemens and is never published.
Maybe IGSS (SCADA from www.7t.dk) still supports the AS511 protocol. They have got a downsized "Free 50" -version in case you want to check.
Kalle
Edit: Ops! I forgot that PI has got an AS511-TCPIP completely magical box that allow you to use S7 protocol on the HMI. If you later convert your S5 PLC program to S7 and keep the DB-numbers, it should be possible to leave the SCADA addressing unchanged.
Link: http://www.process-informatik.de/produkte/s5-lan
Anyone ever set up communications like this? Trying to assist a plc instructor with making a lab up for a local junior college. They have both...
4,363
I have a machine running with a Siemens 627b box pc connected to IO modules via ET200M interfaces and running a WinCC application. There is also a...
3,809
Hello all, just wondering what kind of communication protocols does Siemens PLC hardware speak, example, Modbus TCP/IP, Ethercat, Profibus, ect...
1,169
We have an application where a PC application needs to exchange text string messages with a S7-300 Siemens processor via TCP or UDP...
2,102
This one has been proven to be a real stumper, any help would be appreciated. CPU 316-2 DP When adding a Wincc Flex connection to the existing...
17
6,766