siemens s5 qvz led blinks??
marq
Nov 2003
31
Is it dangerous anyhow? it lits when the plc is on but the controlprogram that runs the system does seem to make eny errors on run allthought the qvz led is blinking??
Only booted up the plc and the control computer, but it works i think im not sure if it always have blinked, does the timeout mean the slow connection between the computer to plc ?
Is that what you get when you try to go online with Step5?
That means that there is no comms between your PC and the PLC. The program has 'timed out' attempting to establish a connection between the PC and the PLC.
Unplug the comms lead from the PLC and plug it back it and re-try.
Paul
I'm not sure... a timeout error between PC <--> PLC is
shown on the screen, but the QVZ-LED too???, I can't remember.
To handle this error you have to create the OB23.
This following text is from a S5-115U manual:
Response to timeout in the case of direct I/O access
The following operations can result in timeout: L PB; LPW; T PB; T PW; LIR; TIR; TNB.
The timeout (QVZ) error occurs if a module fails to acknowledge within 160 µs of being
accessed. The cause may be a program error, a defect in the module or the removal of
the module during the RUN mode. The operating system stores the absolute module
address at which the QVZ occurred in system data word 103 (EACEH) and calls OB23. If
OB23 does not exist, the CPU goes to STOP with QVZ.
HTH
Rolf
Have you changed any wiring, swapped modules or changed your program? The light can blink if you trying to access a module that does exist or needs power connected or a defective module or if the hardware has been changed. Have you checked the I-Stack or B-stack dianostics?
RolfB said:
HTH
Rolf
only the qvz ed, but manual says that it has somethig to do with the timeout?
anyway i want to know is it dangerous, but it seems not to be dangerous for the functioning of our program? am i right?
RolfB said:
HTH
Rolf
o oy the qz ed, but maua ay that it has somethig to do with the timeout?
Marq,
Yes you're right, I remembered what my problem was a few years ago. I replaced an digital input card with a profibus card. The profibus card has to be placed with in the first 7 places in rack 0 (Siemens!!). Everything worked nice but the only thing that blinked was the QVZ led.
Rudi
hi.. Rolf..
I have also the qvz led flashing to fast and i was thinking that can be because i dint conect any device to the analog inputs. is it right ?
my plc is 135u and is runing...
thanks...
From my re-collections of S5, a QVZ error will result in OB23 being called. If OB23 just does a block end, then the plc will carry on running despite the QVZ error. This means that any QVZ error will now be ignored. If your process can afford for any module to fail to respond and not do its job then its safe.
I would remove OB23 which will make the CPU stop, track down the error from the stacks and either correct the hardware problem or remove the software that is accessing the i/o.
Hi! What is the way to convert the code from the Codesys code to the Tia Portal? Regards, WK
72
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
208
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
87
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
173
259