Siemens S5 -> S7 Conversion
mirror_untrue
Nov 2004
Darwin
I am converting a Siemens S5 program to Step7 and a few errors in the conversion need to be manually corrected using equivalent commands in STL. Does any body know what commands can be used to replace the following in Step7
L RS 33
L RS 34
TIR 2
LIR 0
mirror_untrue
The two commands
L RS 33 and L RS 34
Mean that you are loading a word (33 and 34) from the system data range into ACCUM 1
TIR 2 means that you are transfering the contents of ACCUM 2 indirectly into a memory word addresed in ACCUM 1
LIR 0 means that you are loading the contents of a memory word, addressed by ACCUM 1 into ACCUM 1,
In the two above (TIR and LIR) 0 = ACCUM1 and 2 = ACCUM2 for both commands.
As for their Step 7 equivalents, that would depend on the context in what they were originally used and where the data is now stored in the S7 PLC, a L and T command would probably suffice, with a pointer to the correct memory area in the S7.
That's about all the help I can give, without seeing the program.
If I remember rightly, are the system data ranges addressed as S, or as I would call them S flags. I am not sure on that, perhaps someone would like to put me right on that.
Paul
Hi
As Paul correctly stated, RS are system data words.
RS33 & RS34 are address list pointers which show the start address of various block types (in the 135U/150U CPUs anyway)
RS33 = start of FX list
RS34 = start of DB list
(Paul - S flags are the 'extended' flags)
[/B]
If you mean S7-300/400 - no.
krk
Thanks for putting me right on the extended flags, they rang a bell.. but obviously the wrong one. :rolleyes:
jacekd
No I didn't mean S7's, the whole post was about S5's and that was what I was refering to.
Paul
krk, where abouts in Kent are you?
Hi
I have PLC S5 115uU and I try to use CPU S7 414 and S5 I/O rack. When I converter S5 program , i find some eroor for FB 12 ( FIFO ) and Fb 250 ( Read Analog input ) and FB 251 ( Write to analog Output).
Could you help me how can fixed these errors.
My email: [email protected]
Albert
Steveo,
If you want to save some money and time. Look at the Vipa S5 CPU's and the 200 series I/O. If you only have I/O and not CP, IP's or other intelligent cards. this is an inexpensive way to upgrade to a new faster system. Once upgraded then you can rewrite the program at your leisure in step 7 and test it out as you go with their 200 series S7 processors and simply switch back and forth until you have the program converted and tested.
Anyone know how I can convert DTL to DATE type? This rung is trying to determine if the system is in calibration by subtracting the current date...
598
I have converted a Siemens OP7 program to a new Delta DOP107BV. It is all working as expected except for the timer values. I am using MW36 as the...