Siemens S7 400 OB85 trouble
Siemens101
Apr 2009
Alabama
I am not very familiar with S7 so maybe someone can help me out. We had a problem last night with an OB85 I/O failure fault that seemed to correct itself other than the OB85 not resetting. All I/O works fine so we ended up removing a bit from the logic that the OB85 was holding from working. Does this have to be manually reset in the logic? Or will the OB85 reset when conditions permit?
OB85 not only detects I/O faults, but also Programm faults such as non-existant Blocks being called or missing IDBs. To identify the fault you need to examine the local information in OB85.
To help you we need a bit more information and preferably screen dumps and source code.
Daer Siemens,
The operating system of the CPU calls OB85 (if loaded)or goes to stop if OB85 not loaded in PLC:
  • When a start event for an interrupt OB exists but the OB cannot be executed because it has not been downloaded to the CPU.
  • When an error occurs accessing the instance data block of a system function block.
  • When an error occurs updating the process image table (module does not exist or defective).
You can observe what happen by exporting value in OB85 into an MB (programmed inside OB85)
ex:
L OB85_FLT_ID ----> this is the error code
T MB800
then you can see what in MB 800, (possible values: B#16#A1, B#16#A2, B#16#A3, B#16#B1, B#16#B2, B#16#B3, B#16#B4)
The meaning of each code can be read in step7 by pressing F1 in OB85
Regards,
Anton
Thanks Guys,
I return to work Tuesday and I will look at OB85 again and see if the error codes are still there. From what I am hering, they should be.
Thanks,
101
Anton,
Can you tell me a little more about the export and MB thing. I am an s5 guy and this is all new to me. What is MB? And in your example is that a load and transfer (L,T)?
Thanks,
101
Dear Siemens,
S5 FY = S7 MB
Please download S5-S7 conversion from siemens https://support.automation.siemens....tandard&viewreg=WW&objid=10805384&treeLang=en
You can use S5 STL for L and T statement in S7
Put it in OB 85 and check it while online using variable table, I recommend to put the byte into a MB retentive area (must set MB retentive range in CPU properties) and no FC/FB access that byte except OB85. If you find difficulties to set retentive area just create a DB and put it in (usually DB is retentive).
The reason are the byte value won't change except by OB85(OB85 is only called when error happen) or zeroed upon power-off
Ex:
L OB85_FLT_ID
T DB100.DBB0
Then you type in vareiable table DB100.DBB0 and watch online
I believe, if you experienced in S5, S7 will be a piece of cake for you.
Regards,
Anton
Hi, Yesterday, I was at a customer site. I made one little change. Changed a dummy bool output to an actual output. I didn't add any tags, or...
361
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
688
Good Afternoon. I am having a problem going online with S7-400. Attached is the error that I am getting. I have looked at the help file but the...
1,798
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
1,511
I have a project where I've decided to put in a facility to change the PLC time and date through the HMI, as there's no network connection at the...
1,913