i have siemens Siemen S7-400 CPU , and i want to communicate it with S7-300 IO Modules on Profibus Any help would be appreciate as if i have to fetch an analog value from it
There are two ways to do it that come to mind.
1 Master/Master using a DP/DP coupler. This is a device that communicates with both PLC over profibus and uses common memory model where information is written by on plc and read by the other.
2 Master/Slave. This would require a spare Profibus connector on one of the PLCs that can be configured as a slave.
Both methods require changes to the hardware configuration and the writing of code to pass data.
https://support.industry.siemens.co...-400-(master)-with-step-7-v5.3?dti=0&lc=en-US
Nick
Your 400 PLC, is it set up with redundancy? If so, you would need an Y-link.
Do you already have equipment hooked up to it through profibus?
This 300 station, you say IO. Does this mean you only have the IO modules? If so you would need a remote rack or even CPU.
There is a another possibility to the ones mentioned above, No DP, it would allow you to send/receive data directly over the profibus line using S7.
Please do tell us more about your system so we can help you better.
Hi Since last few days we have been facing problem that very frequently some of analog data becomes zero momentarily from a particular remote I/O...
1,269
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
2,842
Hi, I am trying to get communication between Siemens S7 400 CPU & Rotork actuator. I have already installed GSD file in HW config and downloaded...
4,025
Hi, Yesterday, I was at a customer site. I made one little change. Changed a dummy bool output to an actual output. I didn't add any tags, or...
371
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
702