Siemens S7 Addressing
antjon1
Feb 2006
Tennessee
29
Hey, I am in the process of learning how to program the S7 PLC, and I am trying to make sure that I understand how the Siemens addressing works. I am very familiar with AB's addressing, but Siemens is pretty different from that. From what I understand, each card, regardless of how many terminals, has 4 bytes of memory assigned to it. So if there are 4 cards, the 1st and 3rd are input, and the 2nd and 4th output, the addressing would be like this:
I0.0-i0.7, I1.0,
Q4.0, Q5.0
I8.0, I9.0
Q12.0, Q13.0
(All cards are 16 bit)
Please let me know if I am understanding this correctly.
Thanks!
If you have been a little inaccurate and in essence ment to state this
I0.0-I0.7, I1.0-I1.7,
Q4.0-Q4.7, Q5.0-Q5.7
I8.0-Q8.7, I9.0-Q9.7
Q12.0-Q12.7, Q13.0-Q13.7
then you do understand this correctly.
Kind regards,
OK good. Its definitely different from AB. I left off the parts you added in, i ntended them to be there, though, since I am kinda tired right now.
Thank You very much for your help!!!!
Hey Antjon,
You're right about the system default settings. They reserve 4 adressing bytes per digital IO module. However you can override these settings and enter a specific start adress. You can even give the same adresses to both DI's and DO's, so you would get a config like this:
module 1: I0.0-I0.7, I1.0-I1.7,
module 1: Q0.0-Q0.7, Q1.0-Q1.7,
module 1: I2.0-I2.7, I3.0-I3.7,
module 1: Q2.0-Q2.7, Q3.0-Q3.7
On the other hand, when replacing 16DI/DO modules on such a system by 32DI/DO's, the hardware configurator will search for the first 4 available, consecutive addressing bytes:
module 2: Q4.0-Q4.7, Q5.0-Q5.7, Q6.0-Q6.7, Q7.0-Q7.7, <= 16DO replaced by 32DO
(just thought you should know...)
Hi, How to define Siemens(S7-300 via MPI) plc tags in weintek HMI Mt8102? I know Communication is established but i am not defining addresses...
1,751
Hi, How to define Siemens(S7-300 via MPI) plc tags in weintek HMI Mt8102? Communication is established but i am not defining addresses correctly...
1,063
Hi All, In Siemens S7 Classic, if I want to find the location of a physical input corresponding to a peripheral address, (say PIW488), how would...
2,255
Hello guys, This works: L P#DBX 30.0 LAR2 But I need "DBX 30.0" to be input parameter to the function. I made pTag variable with data type...
19
6,389
Hello! I have a database DB1, in S7-1500 PLC with several strings, each with constant size of 64 chars, where I have to send a specify text by...
1,524