Hi, I have purchased 2 x 6ES7 231-7PD22-0XA0, Analog input Thermocouple module, I cannot find any manuals on how to configure thermocouple type (dip switch settings), Thank you
Thanks Nick, I got all the information on page 412 of this manual, Thank you, The worst part is I had this PDF file, just did not dig deep enough, Thanks
No hardware manager in Microwin. Some devices (modems, Motion and comm modules use the config wizards). Thermocouple module takes settings from dip switches. I think you need to cycle power before settings are taken. Addressing grabs the first available Analog input AIW(x), AIW(x+2),etc.
Unit will bring back C or F depending on dip selection as a INT with a artificial decimal offset. Actual Temp = 100.0C, Module returns 1000. Convert from INT--DINT--Real and divide by 10.
Nick
Similar Topics
hey guys here first time for me in this awesome forum actually i have S7-200 connected to Winview HMI and HMI project file has lost and broken...
Replies
0
Views
608
Hi everyone I hope someone would be so kind to help me with this issue, I have trouble finding the way to declare a value which I want to be my...
Replies
1
Views
1,299
Hi everyone Does anybody know if it's possible to connect a termopar to an analog input directly? being more specific Siemens S7-200 analog input...
Replies
2
Views
1,705
Hello everyone, I am quite new both in this forum and in the PLC area. I am happy I found this great forum and hope one day I can help with my...
Replies
3
Views
2,272
I am trying to Configure Siemens S7200 (cpu222) with Vijeo citect scada on PPI cable but the problem i face in vijeo citect is that i am not able...
Replies
0
Views
4,317
Back
Top Bottom