Our system has S7 1516 F CPU. We have doors that have contactless safety doorcontact that is cat 4 ple rated. The sensor provides us with two eqiuvalent safety outputs.
In our safety program we could used the function SFDoor. SFDoor is normally for two sensors on the door. If we use our current sensor in combination with SFDoor, we have no monitoring for discrepancy of the two signals from the sensor. So, is it better to use the EStop function block (that has capability of monitoring discrepancy)?
If we use one of our sensors on one door, what safety category do we reach then? Or, when is it necessary to use two physical sensors on a door?
 
A door normally has open and closed contacts so it can be in the intermediate position of not closed and not open, that is what SFDoor is for. Can you show schematicalyl how your door contacts operate?
 
Is the reason to use the Estop block that the Estop block has discrepancy check (both contacts simultanous) and that SFDoor has that check not?
 
The Euchner switch seems to be an all-in-one device that is not normally intended to be used with an external safety relay.
If you connect it with the safety PLC, then it is similar to cascading two safety relays.
The reset function for the door is in the switch. The safety function in the safety PLC must have auto-reset.
 

Similar Topics

I am working on a program that was developed in 2015 for an S7-300 safety PLC. The new copy of this machine uses an S7-1500 safety plc. We were...
Replies
4
Views
1,915
Hi all! Just got some comments from a client regarding a safety block we made. They want us to replace JMP statements with other logic. They...
Replies
8
Views
2,281
Hello, I'm used to using Allen Bradley RIO options for putting filed IO out in the field and running my safety back to it. Of course I have to...
Replies
5
Views
2,879
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
121
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
210
Back
Top Bottom