hello.
suppose that we have a digital signal that come from a proximity sensor
and frequency of it is 50hz.
we have connected this sensor to one of normal digital inputs of s7-300 plc
and want to calculate frequency.
i am curious to know that if duty cycle of the signal is important or not?
i mean that does the cpu see the signal with duty cycle of 10% or etc?
best regards.
thanks for your reply.
i told s7 plc as an example but my main question is:
The module specifications for a standard 16 channel 24VDC input module says:
input delay for 0-1: 1.2 to 4.8 ms.
what does mean "input delay"?
Does it mean that the cpu don't see signal if width of it be lower than 1.2ms?
best regards.
I go by - the time ON and the OFF time must be as long or longer than the worst input delay plus one scan time.
In your case the input module may not see the pulse if it is less than 4.8 ms. And the signal must be stable at the point in the cycle when it is sampled. Thus my rule above.
Hey all, Before I get started thanks to everyone that has helped in the past. I have yet to have a question that I have not recieved good adivse...
4,422
My Question is: We always have to earth the sheath (protection around the wire's for EMC) on one side of the analogue cable. With Frequency...
20
6,508
I am not sure why this is requested, but it was asked. Currently I have one PLC , with one output to a relay, turning on a field equipment (just...
239
Hi, I am working on automating an industrial fabric shrinkage tester to replace its outdated electronics with a PLC. To get the tank's water level...
17
778
Hello, I have a compact Logix plc and I have been task with configuring alarms into our SCADA when an Analog signal stops moving. The analog...
265