Hi all.

I am using a TP177 Micro and would like to know if there is anyway in which I can change the current active screen from the PLC.
I am used to using Mitsubishi (Beijer) and also Proface HMI and in these I am able to assign a memory location that I can write an integer number to for the current screen to change.
I can also look at another location on these screens for the current screen number.
I am using WinCC Flexible 2005 Advanced and cannot find any information on a function like this. The screen is connectd to a S7-200 PLC.

Thanks in advance

Jonathan Davies
 
Hi,

Yes you can change the current screen from the PLC.
How to do this:
Create tag pointing to memory location of your choice.
For this tag in the properties window > Events > Change value > Select: ActivateScreenByNumber > For Screen number you enter the current Tagname.
Asquisition mode should be set to: Cyclic continuous.

Result: When you write integer to tag, then HMI will active screen with corresponding number. If you write a number to tag and no screen exists with that number, it won't change (or at least it didin't when I last tried it)

If the PLC needs to know the current screen number, this can be done also.
Go to Communication > Connections > Select tab Area pointer. Third line you should see in second colomn 'Screen number'. Now select the connection and the memory location where the HMI should write the screen number. NOTE: This is a 5 word array, it will write 10 bytes, starting from the memory location you defined. If you defined VW0, then VW2 will contain the actual integer screen number.

hope this helps.....

Jeebs
 
The Actual screen number function is not available on the TP177Micro. Your best work around is to NOT USE Goto Screen function ANYWHERE. Use the Tag example shown and change screen based on changed ScreenNumber pointer. Then all Screen Navigation buttons simple change ScreenNumber = New_Value.


Example you want to go to screen #10
Write 10 in PLC or HMI to ScreenNumber and panel will see new value and goto it.

Nick
 

Similar Topics

We have updated s5 to s7200 ,just downloading to the screen TP177 micro using win flex 2005. This will not communicate as the download for the...
Replies
1
Views
5,344
Hello. How to protect access to some views : Hardware : Siemens SIMATIC TP 177micro Software : SIMATIC WinCC flexible Micro...
Replies
0
Views
3,626
I am new to this forum and would need your help. I am looking for the Modbus FBs for the S5 95U for communication with the CP521. These FBs...
Replies
1
Views
39
Hello Everyone Im Trying to Study a PLC programm of a Pet Blower machine, it is programmed in Simatic Manager Step 7 in STL/AWL Lenguage in a part...
Replies
4
Views
72
We are facing intermittent issue with emergency stop and line stop. Line stop triggering with alarm of line stop push button activated at one...
Replies
11
Views
316
Back
Top Bottom