Thanks for reply tharon. According to the manual this should only be an alarm (correct me if I am wrong). At the moment the PLC S7 400 is reporting an external fault every 3 to 4 hours. Below is some of log file from the CPU.
Event 117 of 120: Event ID 16# 2943
I/O access error, writing
P area, byte access, Access address: 3
FC number: 129
Module address: 84
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:17:59.727 PM 10/31/2008
Event 118 of 120: Event ID 16# 2943
FC number: 129
Module address: 60
Priority class: 1
07:17:59.720 PM 10/31/2008
Event 119 of 120: Event ID 16# 2943
FC number: 129
Module address: 84
Priority class: 1
07:17:59.713 PM 10/31/2008
Event 120 of 120: Event ID 16# 2943
FC number: 129
Module address: 60
Priority class: 1
07:17:59.706 PM 10/31/2008
vbmenu_register("postmenu_295585", true);
The alarm is Eb814. The b channel or module is a spare not used.
Question can this still put the S7 400 PLC CPU in fault mode
external fault???
Sorry I can't be of any more help. I've never dealt with Simodrives interfaced with S7 Processors.
There are a few Siemens Gurus around here, hopefully someone can help.
Hello sammy_s;
The diagnostic buffer entry points to an I/O access error from one of your functions (it is requesting data from a non-existing area, or something of the kind.
It also states: Requested OB: I/O access error OB (OB122)
OB122 is a diagnostic OB that is called whenever a specific type of error is detected by the CPU. As described in the Standard and System Functions manual (on your harddisk if you have Step 7 installed):
1.27 I/O Access Error Organization Block (OB122)
Description
The operating system of the CPU calls OB122 whenever an error
occurs while accessing data on a module. For example, if the CPU detects a read error when accessing data on an I/O module, the operating system calls OB122.
The best thing you can do right now is to create OB122 in thre Blocks folder of Step 7 and download it (no internal programming needed) to the CPU. This will allow the CPU to open the OB122 when the I/O access error is detected, and OB122 will be able to gather specific data on the error. Your diagnostic buffer will become much more precise on the occurences that caued the error.
Hope this helps,
Daniel Chartier
dchartier
Thank you for the information that you have supplied which is very useful. Correct me if I am wrong to download an empty OB122.
Today the CPU decided not to go into run. EXTF fault and I have attached the log file not sure if it is related to last week's fault.
Seems like the program's gone!
And yes, you can prevent the CPU from going into STOP just by downloading an empty OB122 (for I/O access errors and/or OB121 for programming errors). But it will not eliminate the problem you have with the drive.
Hey guys im getting some faults with our simodrive 611 and cant seem to find the fault codes anywhere was wondering if anybody could help. The...
3,494
Hi,I have been tasked to upgrade the PLC of a Blowing machine (Gefran) to compactlogix,the machine has Simodrive 611 with CAN bus. My thought is...
1,428
Hi everyone...Can someone give me an idea how to solve the below problem: 1- I'm using a siemens simodrive 611 in one of our machine, 1 of the...
2,503
Dear sir, I have SIMODRIVE 611 universal 6SN1118 2Axes Resolver 611U and I have servo motor with incremental encoder. I need modify the drive to...
1,595
i have a cnc lathe which used simodrive 611 from siemens , we have an orignal card came with the machine about more than 12 years which is...
3,160