Hello all....
Today we replaced a blown out inverter with a SIMOREG DC master unit(132 kW - speed sensing via analog TACHO)). We were able to get the motor running. But when we set the setpoint to the inverter with the potentiometer to let's say 10 % it starts to oscilate around these 10 %. It never calms down so to speak.
We didn't have enough time today to play with all the parameters to fine tune it, so I would like to know if there is something in particular to watch out for.
Any input would be great!
Thanks in advance
Best regards
Ales
You must check thru the instruction manual for Current Loop Tuning or sometimes called Inner Loop Tuning and do that. After that has been done successfully, then you must do the Speed Loop Tuning sometimes called Outer Loop Tuning.
I'm not familiar with the Siemens drive you mention but if it is reasonable new, it most likely will have autotune capability for both of these loops. If you are not experienced at PID tuning, it would probably be best to simply do the autotune and see if it is good enough.
If it is good enough, great. If not, you will need some help to tighten up the speed loop.
Good Luck!
Good Luck!
Even the oldest Simoregs I have dealt with have auto tuning for the curent loop and the speed loop. One is a static tune, one is a rotational. There is also a CEMF tune.
Get the book for the particular Simoreg that you are using, the procedure is spelled out completely in the startup section.
Hi Can someone please tell me where I can find information about the heat developent / dissipation of a Simoreg DC Master? 📚 The information...
940
Hello people This is my very first post in plctalk, so im sorry if my question is out of place. We're using a simoreg dc drive and currently is...
1,526
Dears kindly need support to replace old SimoReg DC master Siemens Drive and upgrade to sinamics 6RA8081-6DV62-0AA0 series communication is...
2,470
Kindly, do you have an idea on how to commission the below two cards, installed on a Simoreg K dc drive ? 6RA8232-1KB0, supplem.board Z1011...
737
Hello everyone. I wish you a good day. I have an S7-300 PLC with my Simoreg DC Master device. Simoreg My device code: "Siemens DC Converter...
2,039