Sinamics and Drive-Cliq problems
userxyz
May 2002
any
2,768
We have problems with a Sinamics Drive-CliQ.
The temperature errors is because of disconnecting the drive-cliq cable. The problems we have is all about the encoder.
We replaced the drive-cliq cable because Siemens tought that would be the cause. But, still problems...
Drive or motor defective... we think the motor...
Anyone had the same probs with Sinamics ?
How often does this occur? Does it occur only when running? Is the DriveCliq away from motor cables?
For an experiment- default the drive and leave the default epos settings
I've seen incorrect settings in the epos mechanical cause odd faults
Other than that, its a very solid system.
Siemens
2 Support Engineers from Siemens came to help us out.
It was the drive-cliq motor. The drive-cliq chip in the motor must have been corrupted.
We placed an other Servomotor together with Siemens and an SMC in between.
The customer didn't have a spare drive-cliq motor with the same proporties, so we placed an SEW Servomotor that we had in spare.
Drive-Cliq motors are a hell when no spare motor, delivery time more then 3 months !!! for such motors.
Is it a drive-cliq motor/encoder or are you using an SME/SMC?
Hy, can we use shielded ethernet cables for drive-cliq connection to sinamics s120 components? Will any problems happen? I contacted siemens...
4,261
Hy, can we use standard ethernet cables for drive-cliq connection to sinamics s120 components? Will any problems happen? Appreciate your help.
5,810
Anyone made their own Drive CliQ cables at lengths of 30 to 40 metres - if so, what cable/connectors have you used ?
8,612
I have G120 with Firmware version V4.7.13. In the TIA project, I have version V4.7.10. I would like to install new firmware HSP in my project. I...
1,911
Hi All I have done the commissioning wizzard on the drive with Tia portal V15.1 and all good , but once i go to acceptance test and click on STO...
2,216