Sinamics G110 auto start
Plavyuk
Oct 2011
Dublin
Hi guys. I replace the faulty inverter on the industrial oven. It was wired for automatic start up , jumper between pins 6 and 3. I did the same but after power down, inverter is not running. Any ideas? I checked the parameters but cant find anything.
Hi
I expect the drive comms preset to use Profibus controls
If using hard wired, look at the I/O parameters for digital inputs section I think it needs to be set to 12 from memory. I usually save the drive config to the op panel..maybe you could check and see if someone else did that before.
We've got to mount a serial comunication between several Sinamics G110 inverters with a RS485-US protocol and I'd like to know if I can give them...