single and differential output sensors.
willpower100
May 2004
B.C. Lower Mainland Canada
81
I recently picked up for evaluation an analag input module made by ICP-DAS, this unit has 8, 14 bit analog input channels. 2 of which are single ended input, and the other 6 are differential input.
My question to all of the minds here is, can I convert single ended output pressure transmitters (4-20Ma, 2 wire) to differential output so that they may be recognized by the analog module.
I understand that the difference between single and differential is that the signal floats and is not referenced to a common ground as in single output. Is there an easy way to simulate a differential output?
Any help would be appreciated.
Willpower
At my plant we have the same model transmitter (loop powered) used in single ended, and differential schemes. The only difference is the wiring. The main difference is the 24Com wiring. I assume the card you are evaluating has a typical wiring diagram. It should show the difference.
I don't know what make/model of transmitter you're using, but I've never encountered a loop powerd transmitter that could not be used either way.
Give me a few more details, and I'll work with you.
Ken
What model do you have, the ones I am familiar with have jumper select to make it 8 differential or 6 differential and 2 single ended.
Ken, thanks for the reply, the sensors I am using are from MSI, the data sheet is at
http://rocky.digikey.com/WebLib/Measurement Specialties Inc/Web Data/MSP-300 Series.pdf
They are 0-5000psig, 4-20Ma output, 10-30Vdc supply, 2 wire transmitter. The manual shows the red wire to the supply, the black wire to the measuring circuit with a common ground. I am using a 125ohm resistor as specified in the analog module manual.
I dont know if I am missing something, it should be pretty simple.
Willpower
I believe the sensor you are using is loop powered, and can be used as either differential or single ended. Your input card should have a wiring diagram for a loop powered differentail input. Just follow that.
Ken
I figured it out myself, it wasn't my sensors or my hookup, but none of the differential channels were enabled. I talked to tech support after I found this out and they said they should have been enabled at the factory. Guess somebody screwed up.
Willpower100
Hi all, I have a PLC5 rack that is actually full(No place for an aditionnal card). The rack has a couple of spare inputs on 1771-IFE cards and I...
3,692
I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit. The problem is that the analog input cards...
156
I actually don't understand which device determines whether the wiring will be single ended vs differential. being single ended or differential...
3,181
Hello, I have a 1756-IF16 configured for single-ended current inputs. I plan to add (4) 4-wire density transmitters. The operating manual for...
2,422
Hello, I am attempting to wire instrumentation to an AB IF16 analog input card. In examining the documentation for the card, I've come to know...
7,201