Sipha 2 control unit
Jun 2021
Turlock
I have a couple questions regarding this safety relay.
First, what does the symbol mean next to the k1 k2 (aux). The one that kinda looks like a Y with the two horizontal lines through it.
Second, I'm not sure that I understand how everything is supposed to work in this diagram. Currently if I supply 24v to 23 and 13, and a momentary pushbutton from x1 and x2, the circuit works as I intend, ie, when the safety inputs are actuated, the outputs (24 and 14) stop working and don't work again until I put them back and hit the pushbutton reset.
I guess I'm just curious for what they are going for in this diagram with the momentary start button and k1 k2 (aux).
They have 2 contactors k1 and k2 breaking the 3 phase power when an emergency is detected. The reset circuit (reset button and 2 normally closed contacts of k1 and k2) is there to make sure the 2 line contactors did open when the emergency happened. so only once they are open and the emergency signals are present wil the reset button reset the circuit
I’m attempt to establish a communication between two simulator M580 CPUs, using a READ_VAR, I have two vitalization Windows 10 in VMWare and each...
53
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
124
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
91
I am not sure why this is requested, but it was asked. Currently I have one PLC , with one output to a relay, turning on a field equipment (just...
219
I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
422