Hello
My problem of the moment is that on our water chiller, which uses an ALLEN BRADLEY SLC 5/02 processor, The first 2 slots are 1746-NT4 cards (thermocouple).
Last week then again late yesterday afternoon the processor went into fault. When I got connected to the processor last week all I notice was the processor status error read
“Specialty I/O module on slot 1 has generated a generic fault. The card fault bit 1 is set (1) in the module status byte”
Now last week I did not investigate too deeply and simply cleared the major errors.
Yesterday I spent some more time checking thing out when I looked at the status words for the slot 1 module all I found was that the second input (input word 1) had detected an open input. With the same processor error.
Now for the questions.
1st Why would an open thermocouple input cause the processor to fault?
2nd Is there anyway in a SLC 5/02 processor to allow for external resetting of major errors so a PC does not need to be connected. It’s not a problem now but in two weeks when I’m away on vacation it could be catastrophic?
We did replace the Thermocouple as well as the 1746-NT4 card to be safe I am planning on testing the card and thermocouple on the bench to see if another failure occurs. I will however have to use a 5/05 processor since I do not stock spare 5/02’s (only got 2 – 5/02 processors on the chillers the rest are all 5/05’s)
Thanks for the help
Michael
My problem of the moment is that on our water chiller, which uses an ALLEN BRADLEY SLC 5/02 processor, The first 2 slots are 1746-NT4 cards (thermocouple).
Last week then again late yesterday afternoon the processor went into fault. When I got connected to the processor last week all I notice was the processor status error read
“Specialty I/O module on slot 1 has generated a generic fault. The card fault bit 1 is set (1) in the module status byte”
Now last week I did not investigate too deeply and simply cleared the major errors.
Yesterday I spent some more time checking thing out when I looked at the status words for the slot 1 module all I found was that the second input (input word 1) had detected an open input. With the same processor error.
Now for the questions.
1st Why would an open thermocouple input cause the processor to fault?
2nd Is there anyway in a SLC 5/02 processor to allow for external resetting of major errors so a PC does not need to be connected. It’s not a problem now but in two weeks when I’m away on vacation it could be catastrophic?
We did replace the Thermocouple as well as the 1746-NT4 card to be safe I am planning on testing the card and thermocouple on the bench to see if another failure occurs. I will however have to use a 5/05 processor since I do not stock spare 5/02’s (only got 2 – 5/02 processors on the chillers the rest are all 5/05’s)
Thanks for the help
Michael