I'm trying to get an OMRON temperature controller transfer output of 4-20ma which is equal to the PV in the system into a 1746-NIO4I module.
I already wired the module and the temperature controller. When I was looking at the PLC, I could see a value changing on the SCP instruction I added but the number that the instruction outputs, doesn't match the PV temeprature from the OMRON control.
Any help will be much appreciated
are your scp min and m ax set up right. For example for an analog signal you have to have scale numbers set for the right values. Look in the manuals they will tell you what those should be at its something like 3277-32768 or something in the ballpark, then you set the bottom two values to display what the temps are going to be for instance 100-500 degrees
I just realize what my problem was. The Scaled Min and Max on my temperature controller was set to -100 - 1500 F and when I set my instruction the Scaled Min and Max I enter where -100 - 800 C.
I was mixing the two scales Farenheits and Celsius causing the strange readings.
It's a good job the PV wasn't -40
You'd have never known there was a problem...
I have a SLC5/05 with a 1746-NI16V. I am trying to configure it for single ended inputs. Please notice in the screenshot the upper SCP is...
21
5,535
Hey guys, Well, the troubleshooting continues for the client who got hit by lightning. New CPU has been installed, and is working! That's the...
3,353
In my 1746-NIO41 analog input card , for a full 20mA input , the reading shows only 16383 ,why is it so ? for input address "i:3.1"
2,005
A unit I work on experienced a lightening strike, andthis resulted in a number of failures. However, I'm puzzled about one issue.. The unit uses...
4,328
Dear , problem : Adding and configuring analog input module 1794-IE8 to existing running system SLC 5/03 through 1747-BSN (DH485) System: - 2...