Slc 500 1746-nt8
nmhandberg
Feb 2019
Minnesota
So i have a 1746-NT8 thermocouple for a conveyor furnace that is causing some problems. When the CPU is in run mode the channel 6 LED flashes, but the other channels are fine. When looking at the HMI it gives good temp readings on everything except for Zone 7 (which would relate to the flashing channel 6 LED due to there being a 0 channel) which is reading ~6000 degrees Celsius. We tried to replace with another 1746-NT8 thermocouple but the same exact problem persisted but this time with channel 0 and 1 flashing and the HMI showing Zone 1 and 2 temps ~6000 degrees Celsius. I am positive the wiring is correct on both.
When running online i get the error shown on the attached image (the thermocouple is in Slot 7 as the error reads).
I would like to note that the thermocouple with the two flashing channels may have experienced water damage from a leak in our cooling process in the furnace. The one with the one flashing channel has experienced no damage as far as i am aware as it was pulled from a spare SLC 500 chassis we had in our store room.
From what it seems to me it is a hardware error of the thermocouple modules but wanted to post here to see if anyone can give me their opinion.
I have attached the .rss file we are using in case it would come in handy.
Thanks,
Nick
  • FURNACE 1 101304.zip
Hi Nick,
Was this a running system or is it a new system you are just now installing?
Have you tried moving channels around? just to see if you get the same error on your system? it maybe wired correct but you may have a sensor failure
Hi Nick and Welcome to the Forum.
Not saying this is your problem but just wanted to pass on an experience I had trying to trouble shoot a similar error. I changed, cards, power supplies even the CPU. Ended up being the back plane.
As I say this may not be your problem but just throwing it out there.
Oh "back plane"!...a memory shoots to the front of my brain...
...now where is it?...
...Ah, here you go...
39281 - Causes and Troubleshooting Error code 55 on SLC500 PLC
Access Level: Everyone
40614 - SLC-5/xx: Error S:6=xx55h, I/O module in slot XX which is required for the user program is detected as having the wrong I/O count
Access Level: TechConnect
Among other things, a backplane issue is a very likely candidate here.
Regards,
George
Hello, We have an old SLC 500 that has two 1746-HS Single Axis Motion Control Modules. One of these modules is bad. Verified by swapping out a...
1,167
Hello, I have a few boards, the same, which are: 1746-OB16/D It seems hard to find the manual online. Any help with that please. My question...
1,272
Hi everyone.. I have 1 basic module SLC 500(1746 Bas), now i want to back up programmed (upload), but i dont know to cumunicate with this...
4,715
Hello all. I have an output module that I'm trying to wire-in and don't know if the module is bad or if the installer (me) has done something...
26
8,642
Hi, I want to set up a remote I/O link between an SLC 5/04 and a remote I/O rack which would be about 100m away (cable distance). I know that I...
3,648