this is just a "wild guess" - feel free to ignore it ...
you aren't (by any chance) trying to read all of this data (from multiple MLX1200s) by doing some sort of fancy "looping" action are you? ...
specifically, are you using 12 separate MSG rungs to do the 12 reads? ...
another thing that I've seen create problems ... sometimes programmers will Copy and Paste the first MSG rung - and then modify the setup from that "starting point" ... I do NOT recommend that - I've seen it cause problems in the past ... specifically, I recommend that you make a brand new rung for each and every MSG - and then enter a brand new MSG instruction on that rung ...
you aren't (by any chance) trying to read all of this data (from multiple MLX1200s) by doing some sort of fancy "looping" action are you? ...
specifically, are you using 12 separate MSG rungs to do the 12 reads? ...
another thing that I've seen create problems ... sometimes programmers will Copy and Paste the first MSG rung - and then modify the setup from that "starting point" ... I do NOT recommend that - I've seen it cause problems in the past ... specifically, I recommend that you make a brand new rung for each and every MSG - and then enter a brand new MSG instruction on that rung ...