SLC 500 SQO and SQC
Les Howle
Nov 2005
Stoke
Can anyone give me an example of using the SQO and SQC functions together
Example
2 Pneumatic cylinders
Cyl A ext
Cyl B extend
Cyl B retract
Cyl A retract
Each cyl driven with double solenoid operated valves
Each cyl equiped with position sensors at each end of stroke
Cycle starts with Start button
I know this is a simple sequence but it will ilustrate the priciple
I have sussed out how to enter the addresses and bit patterns for the
file
mask
Dest
Control
etc
What is confusing me is how to pulse the rung on automatically each time when the step is completed
Cheers Les
With the SQC and SQO, you do not need to pulse the rung on. You only need to place them in parallel on an rung with no input condition.
The SQC will move the control pointer once all the conditions are met and the SQO will move the proper control word to the destination.
I love sequencers!
David
Les, for short sequences I usually abandon the SQC instruction and condition the rung for each step.
I suggest you try something like this and then see how the SQO instruction works. The file N7:20 for this example will look like this
000000
000010
000100
001000
010000
100000
As each step completes, the sequencer will then increment and change the value at N7:0. Once you have the hang of it, then the SQC/SQI pairing will be a cinch.
Another thing you might try is to build a sequencer from scratch using the MVM instruction and indirect addressing - if you can do that, then you have got sequencers down solid.
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
48
1,189
Howdy everyone, My company has a few machines running on SLC500 based PLC, and everytime it makes a part we count up on the counter which gets...
293
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
838
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
1,448
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
606