Marc
Member
Hi guys,
I have an issue with a totalizer (flow GPM) that I created for a customer.
Analog input 4-20ma scaled to 0-200 n15:0
Timer 1 sec dn bit moves n15:0 to f8:0 and adds f8:0 to f8:1 result to f8:1.
F8:1 dislays on a wonderware screen as the last 6 digits of a 2 part combination display (a counter is the first part of the totalizer display to count millions of gallons).
The wonderware display stops at 262144 as well as in the SLC5/04 os 401 series c frn 8. Rslogix500 6.00 winxp. Wonderware 6.0b sp2 nt 4.0 sp4
If I change f8:1 to 262100 it will totalize to 262144 and freeze.
Any ideas?
Marc
I have an issue with a totalizer (flow GPM) that I created for a customer.
Analog input 4-20ma scaled to 0-200 n15:0
Timer 1 sec dn bit moves n15:0 to f8:0 and adds f8:0 to f8:1 result to f8:1.
F8:1 dislays on a wonderware screen as the last 6 digits of a 2 part combination display (a counter is the first part of the totalizer display to count millions of gallons).
The wonderware display stops at 262144 as well as in the SLC5/04 os 401 series c frn 8. Rslogix500 6.00 winxp. Wonderware 6.0b sp2 nt 4.0 sp4
If I change f8:1 to 262100 it will totalize to 262144 and freeze.
Any ideas?
Marc