SLC keeps losing programs upon outages
unsaint33
Sep 2019
MInnesota
118
our SLC5/01 (1747-L511) keeps losing program whenever there is power outage. There is no battery LED warning light. There is no EEPROM. Don't these PLC CPUs keep programs in the CPU internal memory as long as the battery is good?
Yes, an SLC-5/0x controller should keep the user memory in RAM for as long as the battery is good. The modular controllers like SLC-5/01,02,03,04,05 also have a capacitor that can hold the RAM memory for days or weeks.
If your controller is clearing its memory at each power cycle, and no EEPROM is loading an empty program, then both the battery and capacitor have failed and the CPU needs to be replaced.
Any program that runs in a 5/01 will run in a 5/02 or 5/03 as well because they have the same (or larger) instruction set and memory, and a DH485 network port.
Normally, yes.
we had 2 slc 500 plc's that the electronics for the memory capacitors and battery backup components failed due to age or a power spike.
if that happens, the plc will loose the program every time. we sent them to a vendor for repair.
james
We're using a 64K memory SLC 5/04 CPU. One day the program suddenly got erased from the CPU, causing the process to activate the emergency stop...
912
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
93
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
103
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
104
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
96