SLC to CLX migration
smiller
Aug 2003
Arizona/Brazil
116
What would be the options to migrate from installed SLC systems to Compactlogix processors that would utilize the existing SLC I/O.
I have done this with Modicon 984/Taylor Proworx to Quantum/Concept by using a remote I/O head module in the Quantum rack that connects to a remote I/O processor in the 984 rack with good results. Is this approach practical with Allen Bradley?
Thanks.
Steve
You can do this by removing the SLC CPU and replacing it with a 1747-ASB (Remote I/O adapter). Then use a 4-slot CLX chassis and power supply with the Logix CPU and a 1756-DHRIO module.
CompactLogix vs. ControlLogix
mgvol speaks the truth regarding ControlLogix platform. However you mentioned CompactLogix. CompactLogix does not have a DH+ option. Only the ControlLogix platform has the DHRIO card. Same family different form factor. CompactLogix form factor is similar to the MicroLogix. ControlLogix form factor is similar to SLC.
http://www.ab.com/logix/compactlogix/
http://www.ab.com/logix/controllogix/
Regards
That particular combination isn't going to fly.
CompactLogix can support field I/O via EtherNet/IP, ControlNet and DeviceNet.
I know SST is making a Remote I/O Adapter for Compact I/O, but I do not think they are planning a scanner.
1747/1746 I/O systems do not have EtherNet/IP or DeviceNet adapters that can control the I/O racks.
The 1747-ACNR ControlNet adapter only works with SLC ControlNet scanners.
So, you're back to 1756 ControlLogix with a 1756-DHRIO scanner and the 1747-ASB adapter for SLC I/O. It's what Rockwell intends to have you do if you are migrating existing SLC systems.
My bad guys: I guess I focused on the subject line "SLC to CLX" migration a little too much and not enough on the body of the post. OOPS!
I'll start off by saying I'm unfamiliar with communications between PLC's, hence my question here. We have a machine with a ControlLogix & a SLC...
2,796
Anyone know if I can msg between a ControlLogix L71 (A) and an SLC5/05 (C) via backplane of second ControlLogix L71 (B)? ControlLogix (A) and SLC...
2,731
Hi there everyone! Long time lurker, first time poster. I am doing an SLC-5/03 to CompactLogix migration and am having an issue with a barcode...
1,056
Hi All I have been struggling with this problem for a good few hours now without success, so I definitely need some help. I am trying to set up an...
2,265
Hi Everybody, I Am trying to write 10 integers from 1756-L72 (slot 0) with a 1756-ENBT/A (slot 1)to a SLC 1747-L552 over ethernet. Could somebody...
1,764