Have a program running in a plc that a integrator did for one of our plants, and trying to understand it.
It is a slc500, with a 1746-NI16I 16 channel analog input card.
There is a section in the program, which I will attach, where certain bits in a channel are being referenced, that I do not fully understand, and hope someone can explain. I have downloaded the user manual for the analog card, but still not certain what the bits are.
In the attachment, there is the Mov I:1.1 into N12:21
For this to happen, one of the conditions that have to be true is labeled as I1:/285
If you put the mouse pointer over it, it shows I:1.17/13
Do not understand why he did this, it is a 16 channel input card, which I understand to be channels 0-15.
Is I:17/13, which I understand to be channel 17, bit 13 linked to input channel 1?
Will try and read more of the manual, but if someone could point me in the right direction, THANKS
It is a channel status word for channel one for module diagnostics. Bit 13 would mean a faulty calibration. See PDF's below. Programmer does not want to use the data if calibration failed.
Have never used a slc500 with analog before.
Most of my ab experience has been with the micrologix 1200 and 1500.
The way the analog is used is different from the slc.
Will continue to read the manual, but not exactly sure how it could fail the calibration.
Reading more into the manual, and have the following code in the program.
Could someone explain this in simpler terms, having one of those brain dead days, reading it in the manual, but just not quite grasping it.
On first scan of the program (powerup or Program to Run transition) the 1st rung FLL is clearing out all the old data for the 16 inputs. The COP is Writing the Configuration to the module which is stored in Integer file N10:16 to 10:31. To see what the configuration is, you can compare those 16 words to the manual.
The 2nd rung runs continously and is copying the Status Words for each input channel into an Integer file N12:40 to N12:55 for use elsewhere in the program.
Dear Friends, Need your expert opinion. We have SLC500 and installed Analog Output module is 1746-NO4I. Scaling and PID configuration is 0~16383...
1,954
I have two output cards sitting next to each other in a rack: 1746-OW16 1746-OW16 (Octal) output 13 in the first card triggers a solenoid. When...
2,212
PLC SLC5/04 is runing with 1746-NO8I but this module is got defective How can i Use 2 module of 1746-NO4I instead of 1746-NO8I? kindly Help
1,888
I need help in identifying the fault with a 1746-NR4 RTD / resistance module. The hardware is a SLC500 1746-NR4 module inserted into slot 3 of a...
1,297
Here's what I've got... SLC504, 1746-OB16 (Transitor) DC sourcing output module. I'm planning on powering small solenoids with this (I...
3,293