SLC500 Daily Totalizer
cbass
May 2008
BOOKHAM
Trying to get my head around totalizers, instantanious and daily , anyone got some examples for me to look at and crib from ?
I'm totalizing large volume flows, where flows of 400 litre/sec are normal...giving 34560000 litres per day.... then Im going to move this daily total onto an iconics scada. Am I correct in assuming this number ( daily total in Litres) is too big for an N register? and will cause a maths overflow error ( and fault processor) ? what pitfalls should I be aware of if I use an F register for the total value ?
many thanks...
chaz
34,560,000 liters is bigger than you can represent in a 16 bit integer (+32767). Convert to m3 doesn't help in that regard either. Its also big enough that you will loose resoltion in the 1's column of a floating point number, your resolution will be larger than 10 liters, thats not a limitation of the PLC, its a limitation of how floating point numbers are represented.
There are also other issues with accurate totalizing in the PLC that have to do with timing. These have been discussed in other threads on the forum. Do a search on totalizer and totalizing
Forgot to add a picture
What you could do is set up registers to calculate the volume x 1,000, or x 10,000.
For instance, you could set up the logic such that if the volume in your totalizer is greater than 1000, then add 1 to a register designated as (volume x 1,000) or (volume x 10,000) and clear the totlalizer.
This way you can use your totalizer as a count of the volume under 1,000 or 10,000 and you can use the other register in the SCADA and just multiply the value left to get the actual value.
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259
can the slc500 5/05 send a email and text over Ethernet ?
186
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
389
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
2,838
You have to go offline to create the 'Trend' but do you have to download the program to go back Online with the Trend ?
345