This is the problem that I've been encountered for many years. In my shop, I have a SLC500 7-slot rack/power supply and a CPU SLC5/05 with no I/O cards. If I take any real field program and load it into the processor, it will issue a fault (of course, and I knew that). What is the workaround to make the processor disregard the non-existing I/O's and continues to run?
This feature is already existed with the GE9030 PLC. All I have to do is to clear PLC and I/O faults and the program continues to process. Does anyone have any ideas? Thanks.
Don
There's an array of bits in the Status file that enable I/O scanning for each slot in the SLC-500. Turn them to "0" and the controller will go into RUN mode even if the modules aren't present.
Words S:11 and S:12 cover the 30 available slots.
The main drawback is that you can't go into RUN mode if you have more I/O configured than are actual slots in the chassis. My HMI-testing chassis is 13 slots for that very reason. You also can't run if you have M0/M1 file references to a disabled slot.
I thought that I did turn off S11.. before and still didn't work. It sounds to me that my test rack is too short (7slot). I have another 10-slot rack and I will give it a try. Thanks for the tips.
Don
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
292
can the slc500 5/05 send a email and text over Ethernet ?
195
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
400
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
2,861
You have to go offline to create the 'Trend' but do you have to download the program to go back Online with the Trend ?
350