Dear experts,
I have encountered an SMC Flex (361A,480V) wired for 3-wire where that if you press 'Start' Then immediatly press 'stop' it will continue to ramp to full speed before ramping to stop. The display says 'stopping' while it is ramping up. ???
terminal 17 is start button, stop removes power from 17,18. 16 is wired always power (if power is removed from 16, it will ramp to full speed then stop)
I'm not that familiar with these AB drives and I can't find a parameter to address this behavior.
Thanks!
I have encountered an SMC Flex (361A,480V) wired for 3-wire where that if you press 'Start' Then immediatly press 'stop' it will continue to ramp to full speed before ramping to stop. The display says 'stopping' while it is ramping up. ???
terminal 17 is start button, stop removes power from 17,18. 16 is wired always power (if power is removed from 16, it will ramp to full speed then stop)
I'm not that familiar with these AB drives and I can't find a parameter to address this behavior.
Thanks!