How do you feel about splicing wires in condulets with wire nuts, 120vac control wire, THHN wet environment?
Is it normal to tell a guy to move a PB station, knowing and being forewarned that the wires were too short, and then being surprised when he spends 4 hours pulling it though 60 feet of pipe to the nearest j-box which is ceiling mounted in the attic with phenolic block screw terminal blocks.
I was told it was normal just to pull to the nearest pull elbow and splice there. Was I stupid for pulling it all the way back? What do you guys do? Any polices, rules, laws that apply here (aside from the wrong type of wire for water)?
6 14awg wires in a 3/4" plasti-bond pipe tee at the bottom of the drip leg within four inches of the open end (which I also think is wrong, but had no time to fix.) Would you put wire nuts and tape right above a 1" opening near the floor which is sprayed heavily daily?
Is it normal to tell a guy to move a PB station, knowing and being forewarned that the wires were too short, and then being surprised when he spends 4 hours pulling it though 60 feet of pipe to the nearest j-box which is ceiling mounted in the attic with phenolic block screw terminal blocks.
I was told it was normal just to pull to the nearest pull elbow and splice there. Was I stupid for pulling it all the way back? What do you guys do? Any polices, rules, laws that apply here (aside from the wrong type of wire for water)?
6 14awg wires in a 3/4" plasti-bond pipe tee at the bottom of the drip leg within four inches of the open end (which I also think is wrong, but had no time to fix.) Would you put wire nuts and tape right above a 1" opening near the floor which is sprayed heavily daily?