Several months back we installed a Red Lion G315 HMI to communicate with a AB SLC 5/03 attached to the ethernet network via an AB ENI module, using DF1 Master via PCCC/EIP. To date, communication has been fine, until:
We installed a second G315, nearly an exact copy program wise to the same network. These are at our inspection/grading station, not that that is important to you, but that is their general purpose. While both G315's connect and communicate, they appear to lose communication every 10 - 15 seconds or so (data disappears and is replaced with dashes), and then reconnect a couple seconds later (numbers return). They appear to do this in tandem (both at the same time). This is our protocol setup in the G315's:
Enable Device: Yes
Device: ENI/Micrologix
IP Address: 100.100.100.11
Slot Number: 0
Transaction Timeout: 1000 ms
Spanning Reads: Enabled
Transactional Reads: Enabled
Preempt Other Devices: No
Favor UI Writes: No
Comms Delay: 0 ms
Do my settings appear correct? or am I missing something? I do plan on replacing the 5/03 with a 5/05 during the next shutdown weekend, but considering that these G315's replaced two Panelview 1400's that were communicating with the same processor on serial/DH485 with no problems, I have a feeling that the processor change will not correct this problem..... :confused:
I would approach this as a serial bandwidth issue, despite the previous communication method's success.
The Net-ENI has to translate every Ethernet command to DF1 and translate the reply. The effective bandwidth is equivalent to maybe a single 9600 baud link.
I'm not a Red Lion driver expert, but I would recommend adding a "comms delay" to slow down the requests from the two G3 terminals.
I agree that you most likely are limited by the serial speed of the Net-ENI. This would explain why it would work fine with 1 HMI, but when you installed the 2nd one (which doubled the total amount of connections), it gets flaky.
IMO, installing a 5/05 would be the best way to solve the problem. Hopefully you can hop along until then.
Hello every one hope all are enjoying. I have an issue to connect omron NS10 HMI with CJ1M-CPU11 ETN plc I have made all required setting as...
24
Hello guys, I'm working with Emerson's ControlWave Micro and I need to configurate the controller as a DNP3 outstation. It shows me error -8002...
20
So i need to communicate my VFD (LS Electric iS7) with XGL PMEB module i successfully set the gsd file now i cant figure out how the data works...
68
Greetings. I currently have several systems in operation mainly using Aromat PLCs and Beijer Exter HMIs. The HMIs email to VText.com to send us...
61
Hello there, I am having two plcs of mitsubishi (FX5U and R32ENCPU) and one GOT hmi (GS2110 WTBD-N) , I am able to ping all three devices from...
84