STAR DELTA 3 PHASE MOTOR
PERSPOLIS
Jun 2002
ontario
295
HI EXPERTS
SOMEBODY ASKED ME TO CHANGE THE ROATION OF A STAR DELTA 3 PHASE MOTOR
HOW THIS IS POSSIBLE ON A REGULAR DIRECT ON LINE STARTING SYSTEM TWO PHASES ARE INTERCHANGED BUT AS YOU KONW ON STAR DELTA SYSTEM 6 WIRES FROM CONTROL ARE CONNECTED TO 6 TERMAINAL OF THE MOTOR NOW DOES IT MEAN THAT IF I INTERCHANGE TWO WIRES ON EACH BANK THEN THE MOTOR DIRECTION WILL BE CHANGED.
THGANKS EXPERTS
For 415v Star Connection voltage is effectively reduced to 58% or 240v. The equivalent of 33% that is obtained with Direct Online (DOL) starting.
If Star connection has sufficient torque to run up to 75% or %80 of full load speed, then the motor can be connected in Delta mode.
When connected to Delta configuration the phase voltage increases by a ration of V3 or 173%. The phase currents increase by the same ratio. The line current increases three times its value in star connection.
During transition period of switchover the motor must be free running with little deceleration. Whiler this is happening "Coasting" it may generate a voltage of its own, and on connection to the supply this voltage can randomly add to or subtract from the applied line voltage. This is known as transient current. Only lasting a few milliseconds it causes voltage surges and spikes. Known as a changeover transient.
As you can see the supply itself is still 3 phase and if you change any 2 of those you will change direction. The reason for six wires is to convert from star to delta. To understand the connections for this look at:http://www.patchn.com/tutr-mot.htm
you change a normal 3Ph motor by changing two of the phases over
on star/delta you do the same thing but the 2 phases you change on one side you do the same to the other side, or as previously said just change two phases over on the incoming supply.
michael
Dear all Is phase sequence in Star Delta starter necessary, Just i got flash with wrong phase sequence.can anyone tell me how to know the phase...
2,273
Hi, We have a project to replace one Star Delta connection for 90kw motor (3 phase, 415V) with an Inverter. Before dismantle the S/D, the current...
10,561
Here's a question I thought I'd never ask with all my 50 years of experience but I don't know - so I'm asking. I have to change a star delta...
23
3,178
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
2,635
Hi all, Got a customer who's asked me to look at a new machine they've gotten in which they're having trouble starting. It's a brand new...
4,300