Starting an emergency generator
Plc_User
Dec 2005
Belgium
317
A colleage works as electrician in a hospital. They are changing their emergency generator (diesel engine). The diesel engine is started automatically if the normal electrical power goes down. Are there special modules to check reliably the presence of the normal power and that activate the diesel generator is power goes down?
Thanks.
That's usually done with a transfer switch. There should be a "power fail" contact available. You can detect that with a digital input. Typically the generator control and start is done outside the PLC, and the PLC is used for breaker control.
I did some of these installations from the PLC side, 8 seconds to start!
IF I had anything to say about a standby generator in a hospital which is a definite life safety critical piece of equipment for sure
1. I would have reliable automatic controls.
2. I would have manual override with a synch scope to be able to parallel or pick up a dead bus (properly isolated from utility).
To switch bus back to utility would require paralleling for say 30 second and shift load off diesel.
Have seen a case where an emergency diesel did not start - someone unplugged the battery charger. IF my hospital I would have separate battery banks (or air banks in case of air starters) just to make dang sure I can get generation.
Dan Bentler
Dan Bentler
1. What do the drawings indicate?
2. Is there a PM program on this equipment? In our facilities, we have a monthly PM to "test" the generator.
In a hospital scenario, I would definitly want to KNOW if this equipment was functional and reliably operate.
Oakley,
Myself I am not involved in hospital electricity, but what is a
'PM program'. Are there official guidlines for this kind of applications?
Hi, I am attempting to turn on an output for one second, every thirty seconds, but am having some trouble. I have a XIC with S:1/15 (first pass)...
619
Rather new to structured text. I'm trying to edit a machine so that it will reinitialize with some push buttons held in for 10 seconds. Pushing...
2,782
Hi Guys, I'm using an ABL33ER with Panelview 600. I have datalogging running on the HMI using the view studio datalog model on startup of the...
1,163
Hello guys, I have windows 10 on virtualbox guests and not on the host. On a windows 10 guest I have TIA Selection tool V2022.06. When I...
1,530
Hi This message popped up when I created a new hard disk (image) (TwinCat IO Server. TwinCat is not starting because of an invalid device...
1,578