hi , i am trying to have demo unit for sinamics s 120
i have only single phase supply .i need a phase convertor for that . can u recommend one?
yes, you can use single phase supply. S120 demo cases from our siemens guys are all running on single phase, they just use 500W transformer (get's warm) to bump voltage from 120 to 240VAC. but this of course is just enough to power demo with it's small motors. bigger load requires more juice...
dear panic mode
but this will be single phase.
do u have the components of the sinamics s120 trainning case ?
can u send it to me
yes it is single phase, it still gets rectified same way, only the DC bus just gets a bit more ripple. it is a demo case spinning two lightweight plastic discs, not real application of some continuous duty high dinamic servo.
i used to have pictures, manual and circuit diagram of the thing, not sure where did it go. i'll check later on my other machine.
the demo units have:
1x CU320 with basic CF
1x line module (smallest one in 50mm width)
1x dual axis motor module
1x motor with encoder (and DriveCliq interface)
1x motor with resolver (no drive cliq)
1x SMC module (for motor without DriveCliq)
small (too small) transformer
additional I/O (TB31 if I remember)
control unit
remote control unit was in small plastic box with some swithces, LEDs and LCD display (the manual also had schematic)
I have the power supply in the link below. If we want a breaker to isolate and protect the input side how would I size that correctly being 120...
218
I am looking for power supply that I can mount on vertical DIN rail, and when mount that way is =< 4" wide. this is what I have now.... this is...
21
598
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
444
We've still got a ton a PLC 5's installed and running. We lost a 1771-P7 Series B power supply. There are a lot of 1771-P7 series D power...
245
What would happen if you ran a 60Hz Single Phase Motor on 50Hz supply?
552