Switching 2*4-20mA to one AI
MrQ
Feb 2005
236
Hello,
Looking at a system where I need a relay to swith two 4-20mA signals to one PLC AI. Need to be fast and not give any contact bounce, no interference.
Ideas? Anyone who has done anything like this?
Maybe some kind of semiconductor relay?
I have switched 4-20mA signals using a standard electro-mechanical relay. I connected the normal signal to a NC double-throw contacts, and the 2nd signal to the NO contact. It was fast, but not instantaneous, and I did not see any problems with bounce.
I think I used a timer and told the PLC to keep using the last value of the old signal for 2 seconds, and then switched over to the new signal 2 seconds after the relay trigger. In effect, the PLC timer becomes your semiconductor relay.
I may have mis-understood what MrQ needs. I thought it was a case of Either-Or of 2 signals feeding to 1 PLC signal input (switching between 2 signals), not both signals multiplexed in serially one after the other, one-per-time-period.
Or maybe there was only need to switch between two analog signals without multiplexing...:unsure:
More info needed...
Depending on the transmitter you could get an upset if they are loop powered and the loop breaks. Some take a bit of time to re-start.
How about using a voltage input PLC, have both transmitters feed a resistor (250 or 500 ohm)each then switch the voltage signal from across the resistors. The loops stay active and stable. I'd use gold plated relays to cut the noise.
I did it years ago, when AI was expensive and I was out of channels and expansion. In today's world I'm not sure it pays. Having said that, you will need to allow time for the transmitters and signal to stabilize after switching, and you will need to make sure your relays break before make.
Switching should be an absolute last resort. Add an extra analogue input and then do the signal selection within the programming.
Lancie is right about the function:)
And you are all right about that the right way to do this is to install another AI but unfortunately that is not an option:(
If cost prohibits doing this the right way, then simply switch your signal through an ordinary relay and deal with the consequences.
Gold plating is excellent for corrosion resistance but can wear through in time. Silver is more conductive but can be prone to oxidation. Mercury wetted reed relays can provide low current / voltage capabilities even though mercury has less conductivity. Cross bar contact relays can also provide low current / voltage capabilities.
I told the customer that I will not go to the former Soviet republic where the machine will be placed if it runs in to problems due to trying to save one AI and then it was no problem..........
Consider using bifurcated relays for an application like this. It will help ensure the accuracy of your 4-20 over time. We have thousands of these multiplexed I/O points installed and the bifurcated relays really do make a difference in reliability - we learned this the hard way...
Hello guys, please let me ask if you have experience the same situation like this. Inputs are steady but the outputs OTE are switching off and on...
338
is this possible? i have a customer has has a large factory, he has 2 x 800amp supplies coming into the site and would like to switch between...
922
Does anyone have any experience with working on piezoelectric motor control? I want to use off the shelf components to hopefully change the...
745
Hello, I have a Ge Fanuc 90-30 system with a Cutler Hammer PM 3000 Power series HMI. Besides the HMI, the customer is happy with the controls side...
1,013
I'm working with a ROC800 program offline right now. Normally, you can switch your TLP view between text and numbers by making your choice under...
853