# Symbol
The # indicates indirection. I will have to be careful not to explain it wrong, so I'll stop on that subject, but
Also note the size mismatch between the data types. In a COP instruction, the destination determines the size of each element, so if the destination is a Float, thats 32 bits per chunk and five chunks. This means that you are copying 160 bits (10 integers or 5 floats) from the Source to the Destination. In your case the source is a float and the destination is an INT so with a length of 5, you are copying 80 bits, or 2.5 floats!
The COP is a bit for bit image...the MOV will do data type conversion.
Even simpler.....
It indicates that the address you see is the starting point. #F8:61 with a length of 5 indicates that we will start copying at F8:61 and grab five consecutive values. That means F8:61, F8:62, F8:63, F8:64, F8:65 are your source data.
If your destination is #N80:43 then the destination will start with N80:43 and continue through N80:47.
So,
F8:61 is copied to N80:43
F8:62 is copied to N80:44
F8:63 is copied to N80:45
F8:64 is copied to N80:46
F8:65 is copied to N80:47
Hope that helps.
OG
Thanks.
So a copy instruction with the source being #I:1.0, Destination being #N23.0 with a Length of 4.
What would this mean?
Assuming that you meant N23:0 for the destination, 4 elements (16 bit integers in this case) will be copied beginning at I:1.0. Exactly which input words get copied would depend on the I/O configuration of the PLC.
It might be:
I:1.0 -> N23:0
I:1.1 -> N23:1
I:1.2 -> N23:2
I:1.3 -> N23:3
Or:
I:1.0 -> N23:0
I:2.0 -> N23:1
I:3.0 -> N23:2
I:4.0 -> N23:3
Or something else entirely. It depends on what cards are in those slots.
Hello everyone, Recently, my Archestra IDE shut down while I was editing. After restarting the IDE, I noticed warning symbols under my opened...
133
I was looking for this function, so that i doesn´t need to do it in the PLC. If there are an alarm in the alarm list, i want to flash the...
577
Hello, fairly new to plcs I’m tasked with installing a PE to a micrologix1200, in the attached picture I/14 is the PE I’m installing it’s going to...
1,007
Hello Thank you all for your support. I am actually experience same issues with TIA portal V17 update5 as well as V18. The problem is with the...
823
Hi all, I've inherited someone else's program and can't for the life of me figure out his use of the # symbol in one of his structured text...
1,937