Hi everyone,
I'm trying to set up a thermocouple module 1734-IT2I and am getting differential in the temperature reading. What I mean is:
I'm getting from thermocouple 350 counts what gives me 16.6 degrees Celsius (25 counts equals 1 degree) but the real temperature in the room when I work is 22 degrees. What am I doing wrong? Why am I getting different readings?
I've red this literature.
I have thermocouple type J and that's what I set in the module configuration. The module is installed on 1734-MB mounting base with 1734-TBCJC terminal block which I believe has built in CJC. Right now I have CJC disabled. However when I turn the CJC ON the value of "channel 1 data.0" (I have my thermocouple in channel 0) increases from 350 to over 800 (with CJC offset set to default 70 degrees). That doesn't make even more sense cause 800 divided by 21 gives 38 degrees Celsius.
Does the terminal block 1734-TBCJC really have CJC built in or does it have to be the 1734-CJCRTB?
This falls into Mr. Obvious category. But did you use the proper thermocouple wire? You can't just use copper wire. I wired up a thermocouple that way the first time I installed one and got odd readings similar to what you are getting.
Along the obvious line: did you terminate the wires between the thermocouple and the module? You can't just use any old terminals, they must be for the thermocouple type.
Tc positive and negative wiring not reversed any where? A double reverse will show this size of error.
Red is negative.
Are you sure you are looking at counts or are you seeing temperature? Usually the AB TC module converts the input to temperature.....ie 800 = 80.0 Deg.
Red is negative.
I'm looking at the counts at channel data.0 and data.1 and according to AB installation manual 21 counts gives you 1 degree Celcius for type J thermocouple.
How can you at look/see temperature?
Wires are not reversed. I had them reversed at the bigenning and the counts would just go down while the temperature kept going up.
I am pretty sure you see temperature???? You ARE configured for C and not F?
In RSLogix...In the 1734-IT2I module properties box under "configuration", are you looking at "Celsius"?
You will need CJ enabled also for a correct reading.
The Cold Junction Offset should be at 0 unless you find you have to offset it due to calibration errors.
The module IS 21 counts per deg C across the range of -210 to 1200 C, but I still think you are already looking at temperature.
I too struggled with this a while ago
The terminal base required is 1734-TBCJC
this is what BIT me wrong terminal base
Posted by u/mr_biodtox 44 minutes ago Delta ISPSoft - Establishing communication with thermocouple module Hi, How do I establish communication...
343
Hello. PLC beginner here, so apologies in advance for any incorrect terminology or poor communication. I have an SLC 500 Thermocouple/mV Analog...
653
Hello Guys, Trying to scale a thermocouple directly into my IY4 card. Connected into the terminal +\-. I’ve scaled the range of my J type to...
1,686
Hello! I am running a Logix L63 processor with some Phoenix Inline I/O connected over EtherNet/IP. One of the Phoenix modules is a 2 channel...
3,552
I'm doing a small project to read the room's temp by using thermocouple type J. The PLC controller that I have is 1769-L36ERM controller, and the...
41
28,202