IdealDan Member I Join Date May 2017 Location MA Posts 480 Apr 20, 2022 #1 Hi Guys, what could cause HMI Button names in runtime to be showing 'text' instead of their real names. (TIA Portal - Comfort Panel)? I will appreciated your response guys.
Hi Guys, what could cause HMI Button names in runtime to be showing 'text' instead of their real names. (TIA Portal - Comfort Panel)? I will appreciated your response guys.
sigmadelta Member S Join Date Apr 2016 Location From Canada - Living in Bulgaria Posts 2,010 Apr 20, 2022 #2 I believe it's the runtime language selection. You're probably developing in one language, and the runtime is showing another.
I believe it's the runtime language selection. You're probably developing in one language, and the runtime is showing another.
IdealDan Member OP I Join Date May 2017 Location MA Posts 480 Apr 20, 2022 #3 sigmadelta said: I believe it's the runtime language selection. You're probably developing in one language, and the runtime is showing another. Click to expand... Thanks Bro, so I have to change the language on the HMI Hardware or on the TIA Portal (Runtime language settings)?
sigmadelta said: I believe it's the runtime language selection. You're probably developing in one language, and the runtime is showing another. Click to expand... Thanks Bro, so I have to change the language on the HMI Hardware or on the TIA Portal (Runtime language settings)?
sigmadelta Member S Join Date Apr 2016 Location From Canada - Living in Bulgaria Posts 2,010 Apr 20, 2022 #4 Maybe this will help: https://support.industry.siemens.co...-a-simatic-hmi-operator-panel-?dti=0&lc=en-WW
Maybe this will help: https://support.industry.siemens.co...-a-simatic-hmi-operator-panel-?dti=0&lc=en-WW
IdealDan Member OP I Join Date May 2017 Location MA Posts 480 Apr 20, 2022 #5 sigmadelta said: Maybe this will help: https://support.industry.siemens.co...-a-simatic-hmi-operator-panel-?dti=0&lc=en-WW Click to expand... Resolved. Thanks a lot Bro. One more thing please, I have an INT Tag where I moved in values 0 = off, 1=manual and 2=Auto. how can I display the Modes as text using Textlist with the INT tag (Multistate display kind of)?
sigmadelta said: Maybe this will help: https://support.industry.siemens.co...-a-simatic-hmi-operator-panel-?dti=0&lc=en-WW Click to expand... Resolved. Thanks a lot Bro. One more thing please, I have an INT Tag where I moved in values 0 = off, 1=manual and 2=Auto. how can I display the Modes as text using Textlist with the INT tag (Multistate display kind of)?