TSX P57203 processor module issue
MG2020
Sep 2020
Midlands
Hi all, Having an issue with an old Schneider Electric PLC processor TSX P57203. The unit is linked via cable to a Gateway module TSX ETG1010 which in turn is connected via cable to the machine HMI.
The processor has a solid red ERR LED and a solid Amber TER LED illuminated.
The manual description of this LED combination states that a reset is necessary. I have pressed the reset button but nothing has changed.
The Gateway module has a flashing red ERR LED on its display. The manual describes this as a configuration error or the speed between the Gateway module and processor module is different.
Not sure if either or both modules will need to be changed. If the processor has to be changed is it simply a case of removing the memory card from the old one and inserting into the new one once the new processor has been installed on the PLC Rack.
Thanks.
Are you not able to go online with the cpu? Because some more detail of the problem could be seen online
Unfortunately I cannot get online as I dont have access to the software. I have a feeling that the processor module is damaged as the problem arose immediately when the operator turned on the machine after it was shut down for the weekend. The reset button on the module does not do anything either as the manual states that the combination of LED's means the unit needs to be reset. I have located a replacement module online. There is a memory card in the processor. Im hoping that if the processor needs to be changed that it will simply be a matter of swapping the memory card into the new module.
It depends of mem card type.
Flash or bat backupped card.
If whole rack have been without supply and all mem bats are empty, then program is gone.
Is I/O led solid on PLC as it tells also if mem card batteries are empty.
If led is on also on I/O card then there is also I/O errors.
Hi there There is a machine equipped with: P57203 CTX2AY AEY420 x 2 ASY800 DEY64D2K DEY32D2K DSY64T2K DSY32T2K The ERR leds are blinking on...
4,280
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
45
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
139
Hello Dear Experts I have to read 2 words (%MW300 / %MW301) in a M221 plc (TM221ME16R/G) which have a embedded ethernet port. the reader plc...
738
My plc is stx micro 3722 My problem is err led is flashing I tried to re programme my plc with pl7 programme The pl7 tel me cant connect with...
369