Morning All
Quick question.
Building a 250 amp panel, below disconnect is a 335 amp 3 in 6 out distribution block.
I have ten starter/overloads. Is it in code to run two (L1,L2,L3) from one hole to 2 starters.
Thank you for your time.
Take a look at the packaging that the distribution block came in. It will tell you allowable wire sizes and quantities.
I'm about 98% sure it's going to be "no".
You would most likely be better off to buy the feeder buss accessory, if available, to link the tops of your starters together and reduce the amount of wires to the dist. block.
The Cooper Industries (Bussman) data sheet says 1 or 2 wires per terminal depending on wire size. I doubt that the other manufacturers would be any different.
http://www.marathonsp.com/pdf/datasheets/143X553.pdf
Had to figure out what B,C,D,I meant, but according to the PDF (2) # 10 MTW nickle coated copper conductors is allowable per hole.
I was looking more towards the electrical code, but the PDF infers that two wires in one hole is an acceptable practice, then it can also be inferred that it is with in code.
Thank you all for your time and attention.
Have a great day
This is the best answer. You can ONLY do it if the manufacturer of the block has SPECIFICALLY listed the block for accepting more than one conductor per terminal hole. Only that specific manufacturer can tell you this and that information will be on their packaging, a sticker on the side of it, or a data sheet. If it does not SPECIFICALLY state that it is listed for that, then you cannot.
Hi All, I just wanted to confirm something regarding this module. What I understood from the manual, is that if RS-485 mode is selected (jumper...
370
Kindly, we connected electrical power, 3x380 vac, between a supply station and an electric cabinet, away 180 meters. The calculation software...
872
We are in the process of installing a new DC drive to replace a 1373 series Speedpak drive. There are 8 leads coming out of the motor -- Two for...
860
HI guys: I am attaching several diagram from several sources, it seems to be that there is no such a wiring standard for modbus RS485 RTU. In some...
24
4,612
Hi. I always do my best to terminate all cable wires, including unused wires. But I find that it gets difficult when for example I have...
21
8,337