Unable to Upload RSlogix5000
qwemx
Jul 2017
Earth
195
I am trying to upload program from 1769-L32C using RSlogix5000, Communication is established but when uploading it goes through these steps
Connecting to controller
Creating Project
Reading controller status
Ready
and nothing happens
Battery OK stays grey does it mean the program is gone ?
There is a card in the CPU so I believe program should be there
Does the logix5000 version match with the firmware version of the 1769-l32 c ?
Try using the data monitor option in rslinx to check if there is any program in the plc. If a program is in the plc, rslinx will show the tag names & tag values.
What are the Run, OK, and I/O indicators doing? What is your online status? What position is your key switch in?
I think the BAT indicator being grey means there is no trouble there.
https://www.dropbox.com/s/koryxg1zmunschj/vid-20210923-wa0043.mp4?dl=0
tried in all three positions to upload but not able to upload
Run is green when it is chaged to run mode
yesterday contacted the rockwell support
and the engineer told that the compact flash card should also have the program in .ACD file and on checking the compact flash card found there no .ACD file , on checking the data monitor in Rslinx it shows several Tags , upload fails though
the cpu has been powered off for a long time and battery OK is nit green so my conclusion from what rockwell support said that maybe the program has been lost and firmware is 15.31 and rockwell support engineer said only firmware 20.xx can load program from compact flash card
in Rslinx if use the data monitor option tags are visible
but uploading fails could it be because v15 is not supported in Windows 7
yes the battery is not a trouble I assumed that Battery OK should also show green like for example Controller Ok but on reading the manual it says Battery OK when stay grey (off) it means its OK and when there is a problem it will go Red which is not consistent with others like Controller OK going green so I was thinking initially as if battery is Not OK but it is because this indicator goes either Red or stays grey - a bit inconsistent
Hi all, I need some help in uploading of QuickPanel gp570-sc21 program to PC. I load from QP to PC the project through the working HMI-CAB-C49...
2,030
I have a machine that was powered off for repairs, when powered back on the Panelview fails to upload the tag database from the PLC. Its a...
1,542
I was onsite yesterday and had issues going online with a processor. I could see the PLC in Linx, I could go to the webpage in a browser, but in...
1,782
Hello all, I am trying to save a program from a HMI (GP577R-SC11) to QuickDesigner 3.70 and I get an error message at the VERY end saying it's...
4,719
I have successfully established communication using RSLinx class lite and RSLogix starter Micro lite but i am unable to download upload any...
3,044