using ar1
May 2010
ct
I have a small problem, where I am trying to do following:
trying to run a script where it will check for matching input byte number (done in Vat table), and compare it with specific place in DB (expl. DB300.DBD108). If it deasn't find the matching number it will add 30 bytes to last address in DB300 (last address DB300.DBD100) and then compare the byte number from Vat table again, and so on, untill it reaches DB300.DBD318. If it finds matching number then it will copy next 30 bytes from that point in DB300, and place them in DINO with offset of 8 bytes. Here is what I have so far, but for some reason plc exceeds cycle time and goes into stop mode. Can someone give me any pointers to what I might be doing wrong? Thanks
Pointer_Destination and Pointer_Source are ANY pointers
// load the number of FP we are looking for
L #FP_No_Char_1
T LB 4
L #FP_No_Char_2
T LB 5
L #FP_No_Char_3
T LB 6
L #FP_Sc_Char_1
T LB 7
//open DB300
OPN DB300
// start at byte 108
L 108
SLD 3
LAR1
// loop to find matching FP
top: A(
L DID 4
L D [AR1,P#0.0]
==D
JC S001
A(
L 318
SLD 3
TAR1
==D
JC END
L 30
SLD 3
LAR1
+D
LOOP top
TAR1
L #offset_A
S001: L P##Pointer_Source
LAR1
L W#16#1002 //10h for ANY type pointer, 02h for data type BYTE
T LW [AR1,P#0.0] //Transfer to the first part of the ANY Parameter
L 30
T LW [AR1,P#2.0]
L 300 //Load the Data Block number
T LW [AR1,P#4.0]
L P##offset_A //Load the address of the first byte
T LD [AR1,P#6.0]
L B#16#84 //84h is the DB memory area type
T LB [AR1,P#6.0]
L 8
SLD 3
T #Dest_Byte_Offset
// load AR1 into destination db
L P##Pointer_Destination
LAR1
L W#16#1002
T LW [AR1,P#0.0]
// length of copying range in bytes
L 30
T LW [AR1,P#2.0]
// db no.
L DINO
T LW [AR1,P#4.0]
// byte no. of start for db
L #Dest_Byte_Offset
T LD [AR1,P#6.0]
L B#16#84
T LB [AR1,P#6.0]
// BLKMOV
CALL "BLKMOV"
SRCBLK :=#Pointer_Source
RET_VAL:=#SFC20_RET_VAL
DSTBLK :=#Pointer_Destination
END: SLD 0
Your loop top is infinite loop.
Loops work this way:
Code:
     L 10 //load loop count to accumulator
top: T loopCount //transfer accu1 to variable loopCount
     execute some code
     L loopCount
     LOOP top //decrement accu1 by one, if not zero, jump to top
In your case if either of
Code:
L DID 4
L D [AR1,P#0.0]
==D
JC S001
A(
L 318
SLD 3
TAR1
==D
JC END
These conditions will not be true, it will not brake out from loop. Your code seems strange in other ways too, dont have time to check it more now.
You are storing the characters to compare in LB4,5,6,7
This is the local data of the block. You are comparing the chars with DID4, this is the instance data of the block, a completely different area. The comparison should be done with LD4, not DID4
Here's an example FB containing the correct processing:
Code:
FUNCTION_BLOCK FB 5
TITLE =
VERSION : 0.1
VAR_INPUT
  FP_No_Char_1 : CHAR ;
  FP_No_Char_2 : CHAR ;
  FP_No_Char_3 : CHAR ;
  FP_sc_Char_1 : CHAR ;
END_VAR
VAR
  Padding : ARRAY  [1 .. 4 ] OF BYTE ;
  ichars : ARRAY  [1 .. 30 ] OF CHAR ;
END_VAR
VAR_TEMP
  offset_a : DWORD ;
  Pointer_Source : ANY ;
  Pointer_Destination : ANY ;
  dest_Byte_Offset : DWORD ;
  SFC20_RET_val : INT ;
  dwCharComparison : DWORD ;
END_VAR
BEGIN
NETWORK
TITLE =
//copy comparison chars to local dword
      LAR1  P##dwCharComparison;
      L     #FP_No_Char_1;
      T     B [AR1,P#0.0];
      L     #FP_No_Char_2;
      T     B [AR1,P#1.0];
      L     #FP_No_Char_3;
      T     B [AR1,P#2.0];
      L     #FP_sc_Char_1;
      T     B [AR1,P#3.0];
//open DB300
      OPN   DB   300;
      LAR1  P#DBX 108.0;
top:  L     #dwCharComparison;
      L     D [AR1,P#0.0];
      ==D   ;
      JC    S001; //match found
      L     P#DBX 318.0;
      TAR1  ;
      ==D   ; //end of search ?
      JC    END;
      +AR1  P#30.0; //index to next search area
      JU    top;
//match found AR1 point to address
S001: TAR1  #offset_a;
      LAR1  P##Pointer_Source;
      L     W#16#1002; //10h for ANY type pointer, 02h for data type BYTE
      T     W [AR1,P#0.0]; //Transfer to the first part of the ANY Parameter
      L     30;
      T     W [AR1,P#2.0];
      L     DBNO; //Load the Data Block number
      T     W [AR1,P#4.0];
      L     #offset_a; //Load the address of the first byte
      T     D [AR1,P#6.0];
      LAR1  P##Pointer_Destination;
      L     W#16#1002;
      T     W [AR1,P#0.0];
      L     30;
      T     W [AR1,P#2.0];
// db no.
      L     DINO;
      T     W [AR1,P#4.0];
      L     P#DBX 8.0;
      T     D [AR1,P#6.0];
// BLKMOV
      CALL "BLKMOV" (
           SRCBLK                   := #Pointer_Source,
           RET_VAL                  := #SFC20_RET_val,
           DSTBLK                   := #Pointer_Destination);
END:  NOP   0;
END_FUNCTION_BLOCK
I am looking for some advice on this FC I just wrote. I have trace numbers that are constantly moved and want to verify that they match. They are...
5,119
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
64
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
124
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
222
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
60