I was wondering if anyone knows how to determine MCA ( minimum circuit amperage) to so that you know what wire type and gauge to use for things e.g motors etc.

I think that if you have a panel you are supposed to take 125% of the largest motor amperage and then add that will the remaining amperage to find what the MCA is this a true statement?

Also is there a rule of thumb when finding the MCA for field devices like motors and VFD's or am I completely wrong and there is a different process to finding what type and gauge to use?
 
I think you must mean Maximum Circuit Amperage - Also called Full Load Current or Amperage.

There'd be a whole lot of troubles if you chose cable sizes based on the Minimum current.
 

Similar Topics

Hi, I wrote a sequence loop using EQU and MOV instructions and would like to validate that i'm doing this properly. i attached a picture of the...
Replies
15
Views
599
Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
Replies
0
Views
59
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
98
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
160
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
354
Back
Top Bottom