Using Siemens failsafe I/O as standard I/O
doomsword
Aug 2016
Zagreb
201
I have a Siemens S7-414 PLC that has, among other things, one ET200SP rack that has one safety F-I/O card (6ES7136-6BA00-0CA0) (two emergency pushbuttons are wired there).
This card is defined to use PROFIsafe, that since we don't have F or H PLC is impossible (?) to have PROFIsafe, and of course our hardware configuration is now not consistent and cannot be downloaded to CPU.
I'd like to use this card as 'normal' card, to basically disable safety option of this card and just read inputs wired there (of course emergency pushbuttons would be rewired directly to machine to ensure safety). Is it even possible to do something like this?
Otherwise I think this card will be gone, it will be useless to us if we need safety PLC to execute proper emergency pushbutton logic, then we will just do hardwiring and wire feedback about pushbutton status to some other rack.
You cannot use an F-input card without an F-CPU, so yes it is useless to you for your current system.
You would need an F Type CPU to use an F Type input.
If you see the yellow modular slices, then those are the ones for the F Type CPUs.
It's not possible to reassign them to standard type.
I am trying to establish communication between Siemens PLC 1500 and Matlab. I followed a tutorial on youtube at this link: But when I got to the...
375
Context: PLC= S7-1212C, HMI=KTP1200 Basic. Hi, The operator has reported that, from time-to-time, when he presses the "Generate Report" button...
493
I've just created a small program and saved it. Then I clicked on the 'Download to device' icon and this dialogue box appeared. Do I need to...
20
1,462
Hi, Is there an easy way to limit the input tag by using min and max tags from the PLC? Thanks
1,316
I'm using a 3rd party USB to MPI adapter cable. I can see 157 blocks of various types listed under Accessible Nodes in Simatic Manager. The Upload...
28
8,266