Valve Sequence
dskplc
Aug 2013
New Zealand
119
Hello, I am puzzled why my valve sequence doesn't continually repeat since I have a Valve6 timer not done to make it continually run. Please see pictures of my code. I also wrote a simulation routine but thought this was good. I really appreciate your advice. Thank you.
The pictures were pretty blurry, but from the looks of it you need to break the rung that energizes your valve 6 timer. The valve 6 timer is staying energized and preventing the process from restarting. Try putting an XIO for the Valve6.DN bit on the rung with the valve 6 timer.
Then it should keep the rung energized while the timer is not done and deenergize the rung when the timer completes allowing your process to restart.
Another option would be to add this rung:
] valve6.DN [----------------------------------(RES) for the valve6 timer
Better screenshot
Hello Sparkie, Sorry about the blurry pic! I have attached a better one. Thanks. In the meantime I will try what you suggested. :)
Almost there?
Hi Sparkie, Thanks to you I got the sequence to continually go but wondering why the timer for valve 6 doesn't complete my required time of 70 sec but resets at around 10 sec. Please see next screenshot attached. Thank you very much for your help!
Thank you for this. My supervisor said this but I didn't quite understand how to write the PLC code for this but will try to understand. Thanks!
mike dr. Thanks again for the sequence. I was wondering if these open and close are all digital inputs or outputs or both. Right now I have DIs as ValvexOpenFeedback and Dos as ValveOpenCmd. I really appreciate your help.
open and close in the box are Cmd while the conditions are beside the arrow,where you put the OpenFB with timer. for the conditions, do XIC StartPB OTE Trgger.1 then do the state logic.For output, you use XIC state.1 OTE valveXOpenCmd.
mick dr. I got a bit lost in your explanation but have attached my acd file to see if this is what you mean? It is in the routine "scratch". If I use my first idea non-state logic for the valve sequence the timers don't finish the schedule timing and drops out too soon. Not sure why but someone said it might be an input?
you have not answered my question if thats the sequence but as I said, you cant just make the openfeedback your condition of opening/closing the next valve as openFB will turn off once the other valve turns on, which happens on valve6. better to use a MOV state_dint and make that signify what state the program is in and use it as a condition in opening the valve. I cant open your file, don't have that version of RS
Good morning, We've had an issue with a couple of servo valves and was wondering if anyone had seen anything similar. After a drop in pressure...
116
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
180
I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
430
Hi Everyone, Thought I had it figured out but I came to the conclusion it would not work. Here is what I'm working with... 1769-L30ER Flow Meter...
24
726
So I'm pretty green when it comes to troubleshooting in the field so bear with me. We have a Danfoss valve that opens/closes from an analog output...
23
981