Hello everyone,
I need your advice please, all 3 VFD Benshaw RSi S4 are working perfectly until recently. VFD #1 (that is mostly use) has been faulting up on communication loss.
-I should also mention that our customer recently had a power outage
-all VFD's are configured the same
-this drive was also known to fault on Dynamic brake overload (not sure if this is relevant ?)
-we're using Modbus to communicate
-The VFD #3 has recently been powered off.
-The VFD #2 Is working perfectly
One thing that I noticed is that when the VFD drive is running, my PLC has problems pooling the drive, Using message instructions in RSLogix, I get Message errors ("message timed out in local processor"). However 10% of the time pooling the drive is successful.
But while the VFD is Faulted or stopped. The communication to the drive is excellent!! No errors?
Has anyone ever seen a problem like this? What do you think could cause this? Could there be damage to the communication hardware of the VFD caused by the power outage? Or interference?
If VFD #3 is powered off, can this affect the Modbus line since there all connected together?
Thanks everyone!!
I need your advice please, all 3 VFD Benshaw RSi S4 are working perfectly until recently. VFD #1 (that is mostly use) has been faulting up on communication loss.
-I should also mention that our customer recently had a power outage
-all VFD's are configured the same
-this drive was also known to fault on Dynamic brake overload (not sure if this is relevant ?)
-we're using Modbus to communicate
-The VFD #3 has recently been powered off.
-The VFD #2 Is working perfectly
One thing that I noticed is that when the VFD drive is running, my PLC has problems pooling the drive, Using message instructions in RSLogix, I get Message errors ("message timed out in local processor"). However 10% of the time pooling the drive is successful.
But while the VFD is Faulted or stopped. The communication to the drive is excellent!! No errors?
Has anyone ever seen a problem like this? What do you think could cause this? Could there be damage to the communication hardware of the VFD caused by the power outage? Or interference?
If VFD #3 is powered off, can this affect the Modbus line since there all connected together?
Thanks everyone!!