VFD for Vibratory feeder

To the question: Yes.
Depending on the type of vibratory actuator, you may expect regenerative voltage from the drive motor(s). Because of this the VFD must have a brake chopper and a brake resistor.

But in reality: maybe not.
Depending on the conveyor, it may be designed for a specific frequency, and it may break up if you run it at a different frequency. You have to get acceptance from the manufacturer if intend to run it at varying speeds.
Also, if you intend to vary the transportation speed by the VFD, it may not work like that. If you reduce the frequency, the amplitude may increase so that the material transports at almost the same speed.

A VFD to drive a vibratory conveyor has its use for starting and stopping quickly. Especially stopping quickly can be done with a VFD or specialised DC brake devices.
 

Similar Topics

I have a cell with a compact guardlogix as the plc and I have three hmi's and two vfd's on this cell. I been experiencing momentary comms faults...
Replies
10
Views
152
So i need to communicate my VFD (LS Electric iS7) with XGL PMEB module i successfully set the gsd file now i cant figure out how the data works...
Replies
0
Views
72
Hi, I need to replace damage control board of 37kw Danfoss fc360, I have a control board of 30kw of same Model FC360, how to change that board...
Replies
0
Views
66
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
92
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
210
Back
Top Bottom