VFD MD60 AC Drive
peng
Sep 2005
Chicago
48
I have a VFD (Reliance Electric, MD60 AC Drive) running a motor on a system.
Every time I hit stop the VFD goes into a fault (F4-DC bus voltage fell below the minimum value). Every time it goes into this fault, to recover I have to cycle power. I checked the bus voltage and it's fine. Does any one know why this would happen.
peng, I know you said DC Bus Low Voltage but, just to be sure, it wouldn't be DC Bus High Voltage by any chance?
And second, please advise whether the system is configured coast to stop or ramp to stop.
When you say you hit stop, I assume you mean that you remove the run signal from the control input. If you are opening a contactor on the AC input to the drive (not good practice) then I would expect a low voltage fault on each stop. Please confirm your stop method.
Finally, are there any contactors in the leads between the motor and the drive?
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
103
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
237
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
207
84
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
147